I'm also investigating Integrity's Discovery Testing behavior. I've just upgraded to the latest version of Integrity (2.0.0.68). I have the Standard E1.20-2010 choice selected, and it's showing an "Advisory" if I respond to my VENDORCAST. Reading the ANSI E1.20-2010, Section 7.5 says "The DISC_UNIQUE_BRANCH message shall always be sent to the ALL_DEVICES_ID UID Address, since all devices must process this message". Appendix A then defines ALL_DEVICES_ID as 0xmmmmFFFFFFFF where 0xmmmm is Specific Manufacturer ID.. so the Standard seems to say VENDORCAST is legitimate for DISC_UNIQUE_BRANCH. Is this a typo in the E1.20-2010 Standard? and.. is best practice to also ignore VENDORCAST when get the DISC_UNIQUE_BRANCH command?